In-Floor Heating

Heat/AC, electrical, lighting, flooring, design, construction, photos...

Moderator: Team

User avatar
speedtalk
Site Admin
Site Admin
Posts: 979
Joined: Mon Apr 21, 2003 2:43 pm
Location: Kalamazoo, MI
Contact:

In-Floor Heating

Post by speedtalk » Wed Nov 06, 2013 2:55 pm

Anyone have a working setup? Here's where I'm at:
IMG_2735.jpg
You do not have the required permissions to view the files attached to this post.
NEW BOOK:
http://HorsepowerChain.com
Racing Engines Optimized Through Hardcore Math

Don Terrill
SpeedTalk Owner/Admin

PackardV8
Guru
Guru
Posts: 5036
Joined: Sun Jul 30, 2006 2:03 pm

Re: In-Floor Heating

Post by PackardV8 » Wed Nov 06, 2013 8:21 pm

I personally love in-floor radiant heating.

The only drawback I've found is that it doesn't like to go cold at night and then warm up quickly as you walk in the door in the morning.

The upside is when one's feet are warm, the air can be ten degrees cooler and still be comfortable.
Jack Vines
Studebaker-Packard V8 Limited
Obsolete Engineering

User avatar
SWR
Guru
Guru
Posts: 2791
Joined: Sun Jan 29, 2006 5:39 pm
Location: Norway
Contact:

Re: In-Floor Heating

Post by SWR » Thu Nov 07, 2013 5:42 am

I'm going to run the dyno coolant water through the infloor heating system... in the summer I'll just re-route it outside to a big radiator, in the winter I'm not throwing thousands of BTU's out the window...
-Bjørn

"Impossible? Nah...just needs more development time"

Dan Timberlake
Guru
Guru
Posts: 1347
Joined: Tue Jan 15, 2013 8:10 pm

Re: In-Floor Heating

Post by Dan Timberlake » Tue Nov 12, 2013 9:10 am

I assume you are using one of the plastic tubing/pipe products embedded in the floor?

Here in Massachusetts whole neighborhoods of houses built with copper in a floor slab back in the 70s are now having problems.
I'm not sure if it's something to do with long term expansion/contraction cycles, or our water just eating the copper and solder, or even a craftsmanship issue.
Folks are just converting to another heating type and abandoning the embedded system.

cpmotors
Expert
Expert
Posts: 872
Joined: Fri Feb 15, 2008 8:22 pm
Location: Janesville,Wi
Contact:

Re: In-Floor Heating

Post by cpmotors » Thu Nov 14, 2013 2:15 pm

SWR wrote:I'm going to run the dyno coolant water through the infloor heating system... in the summer I'll just re-route it outside to a big radiator, in the winter I'm not throwing thousands of BTU's out the window...
Love It! :D

A friend of mine built his 1800sq ft attached garaged with floor heat and a 50 gal powervent water heater. He only kept it around 62 but it was costing him $3-500 a month. He switched to a wall mounted flash heater and it lowered his monthly costs. I think it would be nice but still have a small furnace to warm the air and circulate it.
Pete Graves
CPMotorworks,Inc.
Custom Engine Machining
Cylinder Head Fixture for Vertical / Surfacing Mills

PackardV8
Guru
Guru
Posts: 5036
Joined: Sun Jul 30, 2006 2:03 pm

Re: In-Floor Heating

Post by PackardV8 » Thu Nov 14, 2013 7:24 pm

Dan Timberlake wrote:I assume you are using one of the plastic tubing/pipe products embedded in the floor?

Here in Massachusetts whole neighborhoods of houses built with copper in a floor slab back in the 70s are now having problems.
I'm not sure if it's something to do with long term expansion/contraction cycles, or our water just eating the copper and solder, or even a craftsmanship issue.
Folks are just converting to another heating type and abandoning the embedded system.
I'm keeping my fingers crossed, but my daughter's house was built in the late 1940s with copper in the floor and it's still working.

We used PEX tubing when we did ours about fifteen years ago and it's supposed to last longer than we do.
Jack Vines
Studebaker-Packard V8 Limited
Obsolete Engineering

User avatar
speedtalk
Site Admin
Site Admin
Posts: 979
Joined: Mon Apr 21, 2003 2:43 pm
Location: Kalamazoo, MI
Contact:

Re: In-Floor Heating

Post by speedtalk » Fri Nov 15, 2013 9:21 am

cpmotors wrote:it was costing him $3-500 a month.
Yikes. That is not going to work.
Dan Timberlake wrote:I assume you are using one of the plastic tubing/pipe products embedded in the floor?
Yes. I could have got a little closer for the photo, but you can see orange pipe.
SWR wrote:I'm going to run the dyno coolant water through the infloor heating system... in the summer I'll just re-route it outside to a big radiator, in the winter I'm not throwing thousands of BTU's out the window...
Great idea
NEW BOOK:
http://HorsepowerChain.com
Racing Engines Optimized Through Hardcore Math

Don Terrill
SpeedTalk Owner/Admin

rce4csh
Pro
Pro
Posts: 204
Joined: Tue Feb 12, 2008 11:24 pm

Re: In-Floor Heating

Post by rce4csh » Sat Nov 23, 2013 11:38 am

The in floor radiant does a fabulous job at heating up the dirt under your slab! Costs a bit to get that done in the form of BTU's and fuel to make em. I have been doing real well with inexpensive hydronic baseboard heaters and a supplemental forced air unit to break the chill in the room. The baseboard units in my 2600sqft shop (metal building) cost me about $125.00 a month to keep things at 65 degrees. The system is flexible enough that I can move the units around with some elementary re-plumbing to accommodate changes in the shop layout over the years. These are just the inexpensive Slant Fin brand units requiring only an occasional cleaning of the fins to work really well. The boiler I use is the forced vent hot water heater unit. I like to mount them in proximity of the larger pieces of equipment in the shop so that I can leverage the thermal mass of these machines. Once they are warm, the boiler seems to cycle on and off much more infrequently.

wagspe208
Member
Member
Posts: 149
Joined: Wed Apr 28, 2010 12:31 am

Re: In-Floor Heating

Post by wagspe208 » Mon Nov 25, 2013 10:44 pm

Man, this could not have popped up at a better time.
Most around here put down 1 to 2" of foam insualtion, vapor barrier, then tubing and concrete. If not, yup... you will contribute to global warming. HAHAHA
I was planning on putting in the PEX tubing.... it is not hugely expensive. My next thought was to do a solar hot water thing....I could build one relatively cheap. I have a waste oil furnace.... if the solar hot water doesn't keep up. I have tons of wood, so an outdoor wood furnace/ boiler would be possible...
The solar hot water would require trhe least amount of maintenance. Turn on pump, thermostat, pump off.
Wags

I am planning on 6" of concrete. That's a big ass heat sink.

User avatar
af2
Guru
Guru
Posts: 6091
Joined: Sun Jan 28, 2007 4:42 pm
Location: Grass Valley, CA :Northern Foothills

Re: In-Floor Heating

Post by af2 » Sat Nov 30, 2013 4:56 pm

Keep the concrete at 2" above the PEX tubing with good underlay insulation and you are good. It does matter the prep in insulating the ground and more so the sides has to the effect on how the system works.

100# water temp should be all you need to make it way more efficient than a forced air equivalent.
GURU is only a name.
Adam

dave brode
Expert
Expert
Posts: 643
Joined: Sun Sep 28, 2008 11:06 am
Location: Frostburg, MD

Re: In-Floor Heating

Post by dave brode » Sat Nov 30, 2013 5:32 pm

SWR wrote:I'm going to run the dyno coolant water through the infloor heating system... in the summer I'll just re-route it outside to a big radiator, in the winter I'm not throwing thousands of BTU's out the window...
Great idea! How hot is the water from the dyno. Could you use the dyno heat to make your domestic hot water in summer too?

The underfloor heat loss issue aside [been covered], on the electric DHW tanks, elec "boilers" etc that have been used to heat the floor: Some guys seem to get caught up in the fact that the slab temp need not be that high. It seems that therefore, they somehow think that an elec tank will do it with ease. It will, but in most parts, elec is the most expensive way to heat the water. It is hard to make some guys understand that it still takes X number of btu to heat the space, period, and elec resistance heat is usually the most expensive choice.

Fwiw, imo, a properly sized boiler is the best choice, natgas if you have it. . The boiler is usually run at it's normal operating temp, and a heat exchanger is and mixing valve is used to give the floor loop the proper temp for the floor. Until the slab heats back up in the morning, a small typical ceiling mounted fan/coil or two can give you quick heat in the morning, using water right from the boiler [not mixed down].

Dave

p.s. - "boilers" heat water, furnaces heat air.....

wagspe208
Member
Member
Posts: 149
Joined: Wed Apr 28, 2010 12:31 am

Re: In-Floor Heating

Post by wagspe208 » Tue Dec 03, 2013 11:24 pm

af2 wrote:Keep the concrete at 2" above the PEX tubing with good underlay insulation and you are good. It does matter the prep in insulating the ground and more so the sides has to the effect on how the system works.

100# water temp should be all you need to make it way more efficient than a forced air equivalent.
I came up with Polyiso something for floor insulation. It is 1.75 thick, so an R10 ish.
Side of slab is against 2x6 wolmaized.... This is a big heat loss? I surely can insulate it... no concrete yet.
"Keep concrete at 2" above Pex tubing...." How critical is this? With insulation below slab I would not have thought much about this.
Thanks
Wags

User avatar
SWR
Guru
Guru
Posts: 2791
Joined: Sun Jan 29, 2006 5:39 pm
Location: Norway
Contact:

Re: In-Floor Heating

Post by SWR » Wed Dec 04, 2013 2:48 am

dave brode wrote:
SWR wrote:I'm going to run the dyno coolant water through the infloor heating system... in the summer I'll just re-route it outside to a big radiator, in the winter I'm not throwing thousands of BTU's out the window...
Great idea! How hot is the water from the dyno. Could you use the dyno heat to make your domestic hot water in summer too?

The underfloor heat loss issue aside [been covered], on the electric DHW tanks, elec "boilers" etc that have been used to heat the floor: Some guys seem to get caught up in the fact that the slab temp need not be that high. It seems that therefore, they somehow think that an elec tank will do it with ease. It will, but in most parts, elec is the most expensive way to heat the water. It is hard to make some guys understand that it still takes X number of btu to heat the space, period, and elec resistance heat is usually the most expensive choice.

Fwiw, imo, a properly sized boiler is the best choice, natgas if you have it. . The boiler is usually run at it's normal operating temp, and a heat exchanger is and mixing valve is used to give the floor loop the proper temp for the floor. Until the slab heats back up in the morning, a small typical ceiling mounted fan/coil or two can give you quick heat in the morning, using water right from the boiler [not mixed down].

Dave

p.s. - "boilers" heat water, furnaces heat air.....

I do a bit of endurance engines that will be tested in loooong slow pulls with everything up to actual running temps of near to 200ºF, so I guess it will be a fair bit of excess heat. How hot it will make the concrete, I do not know, just thinking that anything helps in -20ºC/-4ºF outside temps. Besides, a concrete floor at 60ºF is better than the same floor at 40º, especially if you're sitting on it fixing your DD's brakes or whatever. :)

And I'll make a waste oil burner for the rest of the BTU's needed. That can also be made to heat a big insulated water tank, like a couple thousand liters or 500 gallon one - the Swedes do that with wood - and that holds the heat for almost a week before it needs reheating. Youtube the burner, it's dead simple and you save a buck getting rid of your last oil change.

Might even hook the burner system up to the dyno water through a heat exchanger, so I can pre-heat the engine.. so many possibilities, so little time.. #-o
-Bjørn

"Impossible? Nah...just needs more development time"

dave brode
Expert
Expert
Posts: 643
Joined: Sun Sep 28, 2008 11:06 am
Location: Frostburg, MD

Re: In-Floor Heating

Post by dave brode » Wed Dec 04, 2013 3:09 pm

SWR wrote: so many possibilities, so little time.. #-o
I'll say.

les327
Expert
Expert
Posts: 611
Joined: Sat Jan 12, 2013 8:35 pm

Re: In-Floor Heating

Post by les327 » Fri Dec 06, 2013 9:32 pm

My 40 x60 shop in sc Pa. Has 8- 300 ft. Loops of 1/2 in. Pex pipe and a Munchkin M140 boiler in parallel with a tarm 140k btu wood boiler. I keep floor at 60 degrees F love it. Aprox 200 gal propane 4 cord wood Nov to March. Set up if to lazy to feed wood M140 takes over. So far so good 5 years running i have 6000.00 in heat system. 6`` concrete 1`` extruded foam 6 mill black plastic under 4500 lb. Fibermesh concrete.
A good test is worth a thousand opinions.

Post Reply